Modbus usb to rs232 + rs232 to ttl = timeout....???

Posté : lun. nov. 25, 2013 6:37 pm
par scanbike
I have read a lot on the forums here with google translator. hope someone can English?
I need help to get connected my PHRT 9 ELIWELL ech210bdt Product code MW320252
I connected to the TTL serial port ELIWELL GND = pin1 pin3 TX = RX = pin4 to my RS232 to TTL and RS232 to USB again to my PC with windows 7 (Com 3) open modbus poll but only get timeout ... what am I doing wrong??





J'ai lu beaucoup de choses sur les forums ici avec google traducteur. que quelqu'un peut Anglais?
J'ai besoin d'aide pour se connecter mon PHRT 9 ELIWELL ech210bdt Code de produit MW320252
Je me suis connecté au port série TTL ELIWELL GND = pin1 pin3 TX = RX = pin4 à ma RS232 en TTL et RS232 à USB de nouveau à mon PC avec Windows 7 (Com 3) Modbus ouvert sondage mais seulement obtenir temporisation ... ce que je fais mal? :shock:

Posté : lun. nov. 25, 2013 7:23 pm
par jld82
Hello , good evening

This discussion users fred28 (and bubus) may be usefull for you :
http://www.chaleurterre.com/forum/viewt ... c&&start=0

You can send a "message privé" to everyone perhaps they speek Enghish

Good luck

Posté : dim. déc. 01, 2013 3:23 pm
par bubus
hi

3 other topics:
http://www.chaleurterre.com/forum/viewtopic.php?t=13455
http://www.chaleurterre.com/forum/viewtopic.php?t=13516
http://www.chaleurterre.com/forum/viewtopic.php?t=14801
normally, you have the translate for the 2nd which describe how to establish the com

have you run the loopback test to verify the com with adapter(s) before with Ech ?

what's your request ; try to be more accurate
you can include a copy of different screen:Image

bye

Posté : dim. déc. 01, 2013 8:23 pm
par bubus
bonsoir

copie du MP reçu de Scanbike
"I connected my ECH210BDT to my Pc only get weird values. and time out ....
Windows usb/com settings?
My com to ttl is MAX3232ESE
approx. 6m. cat5 cable to ech210bdt
Image
Image

si vous avez des idées

salut

Posté : dim. déc. 01, 2013 11:11 pm
par bubus
hi

have you run the loopback test on the adapters without connection to ECH

you have only to strap Rx, Tx on adapter
and use soft as"hyperterminal" or equivalent for Win 7
if adapters are recognized, then with "echo mode " disable, any key you press is returned on the pc screen
you can use for com parameters, as for ECH; so, 9600bd, 8 bits data, 1 stop bit, parity even

on one image, vcc seems to be not used (so i think you use wiring with ECH powered by the heating pump) ; maybe you can connect the pin vcc to the correct pin on ECH and test again com

an another thing is the wiring; maybe you can test with shorter wiring on TTL port (and only this connector) and with ECH powered by vcc pin on adapter ; it's not necessary to turn on ECH, in this case only decimal point is lighted

to valid the modif H26,H44,H45 you have also to turn off Ech (press >2" down arrow to turn off and the same key to turn on)
the timing should be:
modif these 3 param
turn off ECh
install com wiring with adapters
turn on Ech
start com soft

Image

sorry for the brain storming!
bye

Posté : lun. déc. 02, 2013 11:55 am
par bubus
hi

could you send us an image of the "device manager" screen when the 2 adapters are connected ? (specially usb controller)

to verify if logical controller inside usb/rs232 adapter is "prolific" or "fdti" or other

thanks
bye

Posté : mer. déc. 04, 2013 12:33 pm
par bubus
Hi Scanbike

as you are connected, com with ECH is still wrong ?